Paula Levesque

Today in fire history: fire in a restaurant caused by 20-pound LP-Gas cylinder

Blog Post created by Paula Levesque Employee on Jul 30, 2014

SeasideParkJuly30
Shortly after 7:00 p.m. on July 30, 1985, a fire erupted from beneath a steam table located inside the main dining room of the Bayview Restaurant in Seaside Park, New Jersey.  At the time the fire broke out, between 75 and 80 patrons were in the room of fire origin, and all of them, including employees, and two occupants of the second floor narrowly escaped.  Upon fire department arrival, flames were coming out of the window openings, and an adjacent two-story residential unit was beginning to burn.  Fire fighters successfully provided exposure protection and extinguished fires in the adjacent residence.  A large part of the restaurant, however, received heavy fire damage before final extinguishment.

The Ocean County Fire Marshal has determined that the fire was caused when a flexible metal hose, connecting a 20-pound LP-Gas cylinder to a steam table, failed allowing LP-Gas to escape.  Ignition quickly followed, producing intense flame which spread rapidly to adjacent combustible interior finish within the dining room.

NFPA 58, Standard for the Storage and Handling of Liquefied Petroleum Gases, with minor exceptions, prohibits the use of LP-Gas cylinder inside buildings.  This incident clearly demonstrates the extreme hazard that improper use of LP-Gas can pose to life and property, and the importance of complying with the provisions of NFPA 58.   

For more information on this fire NFPA Fire Investigations.  To learn more about NFPAs Fire Analysis and Research statistical report on Eating and Drinking Establishments. For Free access to the 2014 edition of NFPA 58.

Outcomes