During today's NFPA Technical Meeting in Chicago, the following action has taken place on NFPA 652, Standard on Fundamentals of Combustible Dusts:

 

•    652-1 Motion to Accept Public Comment No. 483 was not pursued.

•    652-2 Motion to Reject Second Revision No. 40, thereby deleting new section 7.1.1 was not pursued.

•    652-3 Motion to Reject Second Revision No. 41, thereby deleting new section 7.1.2 was not pursued.

•    652-4 Motion to Reject Second Revision No. 44, thereby deleting new section 7.1.1 and A.7.3.1(2)(b) was not pursued.

•    652-5 Motion to Reject Second Revision Nos. 40, 41, 42, 43, 44, 45, 46, 47, 143, 49, 66, and 203 including First Revision Nos. 67, 68, 69, 72, 70, 71, 74, 75,. 76, 77, 73, 78 and 99, thereby deleting Chapter 7 failed.

•    652-6 Motion to Accept Public Comment No. 625, thereby returning the entire standard to the Technical Committee failed.

 

NFPA 652 was passed with 0 amending motions. NFPA 652 COMPLETED.

A frequent question I get is whether NFPA 495, Explosive Materials Code, requires the installation of sprinklers for a commercial stock of smokeless propellant at a location. The trigger for requiring sprinklers in this situation can be found in 14.3.9(5)(h), when you are storing above 800 lb but below 5,000 lb inside a building. At this point you are then required to have a sprinkler system that is installed according to NFPA 13, Standard for the Installation of Sprinkler Systems. This requirement can be ignored if stored according to 14.3.8(6) which requires a Type 4 magazine constructed and located in accordance with Chapter 9, Aboveground Storage of Explosive Materials.

 

-Eric Nette, P.E.