Question asked by kerrie on May 18, 2020
Latest reply on May 18, 2020 by cdafd

Does anyone know of a company in the New England area that tests (lab tests) fixed temp non restorable heat detectors that are expired? Never had a customer come back and want this option but here we are

No restorable fixed-temperature, spot-type heat detectors are required to be replaced after 15 years from initial installation [see NFPA 72 (13), Table 14.4.2.2, Item 14.d.3. As an alternate, 2 detectors per 100 must be laboratory tested (the two detectors must be replaced with new devices).