Maximum velocity of 20 ft/s in fire protection sprinkler piping systems. Is this acceptable?

Question asked by rick.nunez.3000 on May 8, 2020
Latest reply on May 22, 2020 by rick.nunez.3000

Per NFPA 13 (2020 edition) and earlier versions, the maximum velocity limit in the fire protection system pipings has not been specified to be limited up to 20 ft per second.  Since it is unspecified, it follows that a designer could impose a velocity exceeding 20 fps, say 30 fps, and his design would still be safe. 