What is the minimum PPE Category required for removal and insertion of an individual starter bucket in a 480V motor control center?

Poll created by dvigstol Employee on Nov 16, 2017

Using the PPE Category method for determining the appropriate level of PPE when performing justified, energized work, what is the minimum PPE Category required for removal and insertion of an individual starter bucket in a 480V motor control center? The available fault current is 45,000 amps and the upstream OCPD clearing time is .1 sec or 6 cycles. Working distance is not an issue.

 

Vote below, and stay tuned for the answer on Tuesday, November 21st!

2 total votes
  • PPE Category 2
    0
    Your vote
  • PPE Category 3
    0
  • PPE Category 4
    1
  • The PPE Category method cannot be utilized
    1