Underground Conduit - Encase or Direct Burial? (NEC 300.5)

Discussion created by Kedwin Dominguez on May 17, 2017
Latest reply on May 19, 2017 by Kedwin Dominguez

Design scenario:

Conduit has to be installed from a pad mount transformer secondary to a electrical room (MCC).  In between has no traffic and is a industrial location.  

 

-------------------------------------------

Applicable Code (NEC 2014)

-------------------------------------------

According to 300.5 

(C) Underground Cables and Conductors Under Buildings.
Underground cable and conductors installed under a building
shall be in a raceway.

 

According to Table 300.5 Note 2

2. Raceways approved for burial only where concrete encased shall require concrete envelope not less than
50 mm (2 in.) thick.

 

My questions is:

  • If conduit is installed underground, is it safe to assume the conduit will always be concrete encased? if not, when would be the exception?

 

Thank you for your assistance,

 

Kedwin Dominguez