AnsweredAssumed Answered

What is the water supply duration for a rubber tire storage using a ESFR sprinklers?

Question asked by ileon on Sep 29, 2017
Latest reply on Sep 29, 2017 by cdafd

The NFPA 13 2016 edition stablish a 180 duration for a rubber tire storage with a ESFR sprinklers, but a old version stablish a 60 minutes. 

There is a TIA Log No: 1227, reference table 12.8.6. comment closing date: July 12, 2016, submitter: Larry Keeping, PLC Fire Safety Solutions, and I want to know if this  documment apply to the duration of the water supply. Document TIA Log No 1227

Outcomes