Trapeze Hangers are sized using a tabulated Section Modulus. Can I size Trapeze Hangers computing a Section Modulus by me using the same values used to calculate the tabulated Section Modulus?

Question asked by sti on Jul 3, 2018
Latest reply on Dec 20, 2019 by gbartels

From NFPA 13 - 9.1.1.2, We Know that Hangers shall de designed to support five times the weight of a water filled pipe plus 250lb (115kg) at each point of support.

 

But in 9.1.1.7.1, Trapeze Hangers are sized using a tabulated Section Modulus calulated on a maximum bending stress of 15ksi (103MPa) and a midspan concentrated load from 15ft (4,6m) of water filled pipe, plus 250lb (115kg).

So when I design a Trapeze Hanger I can size it computing a Section Modulus using the Load of water filled pipe plus 250lb (115kg) and a maximum bending stress of 15ksi (103 MPa), right?