AnsweredAssumed Answered

NFPA 850 TURBINE FIRE PROTECTION

Question asked by iyvf on Aug 27, 2018

Hey!

I have few questios about NFPA 850.

First.

Does the 7.7.3.6 indicates that I have to comply with all the 5 items there or if I have one of them I´m in accordance with that paragraph?

 

Second.

7.7.4.1.1 indicates "All areas beneath the turbine-generator operating
floor that are subject to oil flow, oil spray, or oil accumulation
should be protected by an automatic sprinkler or foam-water
sprinkler system. This coverage normally includes all areas beneath
the operating floor in the turbine building. The sprinkler
system beneath the turbine-generator should take into consideration
obstructions from structural members and piping and
should be designed to a density of 0.30 gpm/ft2 (12.2 mm/min)
over a minimum application of 5000 ft2 (464 m2)."

 

This means that if I DON´T have anithing beneath the turbine that can cause a fire I DON´t have to protect this area, right?

Attachments