sizing a nipple between 2 panels

Question asked by cowboy19666 on Dec 15, 2018
Latest reply on Dec 27, 2018 by jmueller245

I have 3 500 THHN .7073 sq. in area and I choose a 2" EMT AS THE RACEWAW WITH 2.013 Sq. in. area, and I use chapter 9 note 4 that allows me to fill the conduit to 60%, am I correct? because this looks like it's too small, but I'm doing practice quizzes on line and the person is saying 2" EMT IS THE CORRECT SELCTION?