Is it allowed to install the Foam bladder tank inside the room they protect?

Question asked by ashikpn on Apr 16, 2019
Latest reply on Apr 18, 2019 by nocivus

Is it allowed to install the Foam bladder tank inside the room they protect?

As per NFPA-16 5.9 :Equipment items, such as storage tanks and proportioners for foam concentrates; pumps for water and foam concentrates; and control valves for water, foam concentrates, and foam solution, shall be located as near as possible to the hazard or hazards they protect but shall not be exposed to a fire in a manner that is likely to impair system performance .

However, It is not clear that it is allowed to locate the bladder tank inside the room they protect unlike as per NFPA-2001 for clean agent systems.4.1.3.2* Storage containers shall be permitted to be located within or outside the hazard or hazards they protect. fixed foam system