312.2 damp and wet locations

Question asked by charlesvanmeter on Nov 17, 2019
Latest reply on Nov 19, 2019 by brianbaughman

312.2 says in wet or damp locations to cabinet or cutout boxes shall be mounted so there is at least 1/4 inch airspace between the inclosure and the wall or supporting surface. My question is how to achieve this spacing on the outside of the residence with siding? in the past I have put a piece of plywood behind the panel and then used spacers made of 1/2 inch pvc conduit or on a brick wall use the same spacers. Does anyone have any other tricks of the trade they prefer to use to achieve this spacing?

Thanks