AnsweredAssumed Answered

Perfect Fry Machine Listed under UL 710B and by ETL

Question asked by rfoxfire on Feb 29, 2020
Latest reply on Mar 2, 2020 by rfoxfire

Listed under UL197/UL710B -NFPA 96 states in 13.1.(6) "Fire Extinguishing Equipment complying with requirements of Chapter 10  with the exception of 10.1.1 & 10.5.1 which shall not apply."

1. Therefore A Type K Extinguisher is required? "10.2.1 Fire-extinguishing equipment shall include both automatic
fire-extinguishing systems as primary protection and portable fire extinguishers as secondary backup.
10.2.2* A placard shall be conspicuously placed near each Class K extinguisher that states that the fire protection system shall be activated prior to using the fire extinguisher."

2. 10.6.2 Where a fire alarm signaling system is serving the occupancy where the extinguishing system is located, the activation of the automatic fire-extinguishing system shall activate the fire alarm signaling system.

Or:

Does the UL 710B Listing say otherwise?  I see that to purchase a copy of the listing from UL is between $1000.00 and $1500.00!