Foam Sprinkler Test connection

Question asked by ashikpn on Sep 6, 2020
Latest reply on Sep 6, 2020 by nocivus

Dear all , 

 

Good Day , 

 

one of the ongoing project , i have to provide a test connection for periodic inspection in Foam sprinkler system main riser after the proportioner. my basic question is , what is  the size would be ? please suggest. 

 

For Example 

Foam system main Riser Pipe dia is 3" or Greater, shall i consider same size as Main riser or Can i go with 1" 

 

NFPA 16 Saying in test connection 5.14

system test connection shall be sized to accommodate both the low flow of proportioner and maximum anticipated flow through the proportioner